setting charge period 2 times to Octopus intelligent time slots #11

Answered by canton7
Alllfff asked this question in Q&A
Discussion options

You must be logged in to vote

I would like an automation to take the start and end time stamps of the "off peak" slot from Octopus Intelligent HA integration and fill them in the times of the "charge period 2" times in this integration, any way to do this please? Thank you

You'd do this by calling a service from the foxess_modbus integration, not by using the charge card (which is just UI). There's a service you can call to set a charge period, and pass the start/end times from the Octopus integration. I think nathanmarlor/foxess_modbus#404 was doing this?

On another note, I can set the work mode of the Foxess to "Back up" by an automation which will prevent the EV draining the home battery but this will not allow …